I’d like to add a couple of sensors to my yard gates that do not get activated when the alarm system is armed. I just want to have open/close notifications on the gates regardless of system state. Can someone point me in the right direction? I have a GC3 panel.
A good option for this purpose would be the Honeywell 5816OD outdoor contact.
Sensor Type: 23 - No Response Type
Sensor Equipment Type: Contact
Equipment Code: Existing Door/Window Contact
Serial Number: Learn – Trip Sensor
Equipment Age: New
Sensor Loop: 2 (or Loop 1 if using it as a transmitter for a different wired sensor)
Transmission Delay: Disabled
Voice Descriptor: As Desired
Sensor Reports: Enabled
Sensor Supervised: Enabled
Sensor Chime: As desired
Thanks Jason. I had purchased a couple of 2GIG recessed door contacts. I am able to add them to the panel, learn the serial number, but I cannot get them to trip. I’ve tried putting them in as an entry/exit type as well but whatever I do I cannot get them to trip open/closed. What could I be doing wrong? I’ve set them up exactly as shown in your response except for putting them in specifically as the recessed door type for equipment code.
I had purchased a couple of 2GIG recessed door contacts.
To clarify, are these for a different purpose than what was originally requested in this thread?
The DW20R will likely see its lifespan affected by use in a completely unregulated outdoor environment. It would be better to use outdoor sensors as described above.
The Loop number programming is different depending on the model of sensor.
Thanks Jason - putting them on loop 1 solved the issue. I already had these on hand so I will see how long they last outside. Hopefully being embedded in the gate will afford them some protection and they will last a while.
Humidity and temperature will be an issue in the long run. I couldn’t say how long they will last, but it will depend on how well it is sealed in there.